Electrical Tool: How to Use a Megger (Insulation Resistance Tester)

Electrical Tool: How to Use a Megger (Insulation Resistance Tester)1730 作者:APPZZ 帖子ID:117
A Megger produces high voltage and very low current, so safety is important.
Never touch both test terminals with your hands during operation.

1. Checking Whether the Megger Works ProperlyStep 1 – Open-circuit test
Connect the Megger leads to a multimeter (voltage measurement).
Rotate the handle — the voltage indication should rise steadily as the generated voltage increases.
On the Megger scale, the pointer will move toward infinity (∞).
Step 2 – Short-circuit test
Short the Megger output terminals together and rotate the handle.
The pointer should swing toward 0 Ω.
If both behaviors are normal, the Megger is working correctly.

2. Testing a MotorA. Insulation between winding and motor frame (check leakage)
Do NOT remove the copper links on the motor terminals
(horizontal links = star connection, vertical links = delta connection — either is fine for this test)
  • Connect one Megger lead to any phase terminal
  • Connect the other lead to the motor housing
  • Rotate the handle

Result:
  • High resistance (near ∞) → Motor insulation is good
  • Low resistance → Motor has leakage to ground


B. Insulation between phases
  • Remove the copper links
  • Connect leads between U and V, rotate handle
  • Then test U–W and V–W

Result:
  • High resistance → Normal winding insulation
  • Low resistance → Winding insulation damaged


Notes
A Megger provides much more reliable insulation testing than a multimeter.
It is commonly used when a multimeter cannot accurately determine motor condition.